N nizak Senior Member Jul 24, 2024 #1 Can a residence have 2 Emergency Disconnects ? or does it need to be just one? 2- 200 amp panels fed from a 320A meter base. One disconnect for each panel.
Can a residence have 2 Emergency Disconnects ? or does it need to be just one? 2- 200 amp panels fed from a 320A meter base. One disconnect for each panel.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 24, 2024 #2 I would think that two are okay, as long as they're grouped.
J John A Member Location New Jersey Occupation Inspector Jul 24, 2024 #3 I know of no reason two can not be installed off af a 320. Common here for McMansions.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jul 24, 2024 #4 The rule in 230.85 says: If more than one disconnect is provided, they shall be grouped. Click to expand...
The rule in 230.85 says: If more than one disconnect is provided, they shall be grouped. Click to expand...