Emergency egress lighting remote heads
scott3104
I can't find the code article that tells what wiring method to use for remote battery heads on emergency egress lighting systems can anybody help me?????
Re: Emergency egress lighting remote heads
700.12 (E) (4)
shall have all wiring to each unit installed in accordance with the requirements of any of the wiring methods in chapter 3.
look in chapter 3 of the NEC.
it's there just like it has always been.
along with tons of other wiring methods.
Article 320 Armored Cable: Type AC
Article 322 Flat Cable Assemblies: Type FC
Article 324 Flat Conductor Cable: Type FCC
Article 326 Integrated Gas Spacer Cable: Type IGS
Article 328 Medium Voltage Cable: Type MV
Article 330 Metal-Clad Cable: Type MC
Article 332 Mineral-Insulated, Metal-Sheathed Cable: Type MI
Article 334 Nonmetallic-Sheathed Cable: Types NM, NMC, and NMS
Article 336 Power and Control Tray Cable: Type TC
Article 338 Service-Entrance Cable: Types SE and USE
Article 340 Underground Feeder and Branch-Circuit Cable: Type UF
Article 342 Intermediate Metal Conduit: Type IMC
Article 344 Rigid Metal Conduit: Type RMC
Article 348 Flexible Metal Conduit: Type FMC
Article 350 Liquidtight Flexible Metal Conduit: Type LFMC
Article 352 Rigid Nonmetallic Conduit: Type RNC
Article 353 High Density Polyethylene Conduit: Type HDPE Conduit
Article 354 Nonmetallic Underground Conduit with Conductors: Type NUCC
Article 356 Liquidtight Flexible Nonmetallic Conduit: Type LFNC
Article 358 Electrical Metallic Tubing: Type EMT
Article 360 Flexible Metallic Tubing: Type FMT
Article 362 Electrical Nonmetallic Tubing: Type ENT
ABOVE REFRENCED SECTIONS are from 2005 NEC
Whatever method you choose the conductors from output of the EBU must remain separate from the rest of the wiring systems.
Separate boxes, cables, raceways etc.