I am currently in a debate about the proper way to feed fluorescent troffers with integral battery backup utilized for emergency egress lighting and exit signs in a typical office space.
NEC 700.12(E) states, ?The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.? This indicates that, excluding the exception to this paragraph for three or more lighting circuits in a uninterrupted area, it would be against code to employ a single circuit (with padlock provisions) utilized as a night-light circuit to power the emergency light fixtures. It has been argued that you are required to feed the emergency lighting fixtures separately from the normal lighting circuits in this manner by NEC 700.9(B) which states that ?Wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment?.
Any code references that clear this up would be appreciated.
Thanks.
NEC 700.12(E) states, ?The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches.? This indicates that, excluding the exception to this paragraph for three or more lighting circuits in a uninterrupted area, it would be against code to employ a single circuit (with padlock provisions) utilized as a night-light circuit to power the emergency light fixtures. It has been argued that you are required to feed the emergency lighting fixtures separately from the normal lighting circuits in this manner by NEC 700.9(B) which states that ?Wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment?.
Any code references that clear this up would be appreciated.
Thanks.