Is it against code to run coduits containing normal power through an emergency electric closet?
Not in the same raceway though.Maybe explain what it is you are calling an "emergency electric closet" and we may be able to better answer the question.
If what you have is a room that only contains emergency equipment items it may be good design practice to keep normal power items out of that space but isn't necessarily a NEC violation either.
yes.Not in the same raceway though.
The OP is in MA, in MA the rules require two hour fire seperation of emergency transfer and distribution equipment.
I don't have the MA amendments handy so I can't post them or even look at them right now.
I pretty sure the answer to the OPs question is no, you can't run normal power inside the emergency elecrical space.
Yes I agree it's not the best practice and I know you can't run in the same pipe or j-box however As is the case most of the time I have little to no room I my electric room and the emergency closet containing a high and low voltage emergency panels is a room inside the normal electric room so running normal power conduits through the room may be my only option. I could not find a code violation and just wanted to know if anyone has done this before. Thanks