Emard

New member
When wiring emergency/exits in a non emergency backed up commercial application must you wire each emer/exit light off the lighting ckt. of the particular space/room it occupies. If so where in the code is it stated. Can it just be run on a dedicated emergency ckt. that daisy chains from one room to anothet?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
When wiring emergency/exits in a non emergency backed up commercial application must you wire each emer/exit light off the lighting ckt. of the particular space/room it occupies. If so where in the code is it stated. Can it just be run on a dedicated emergency ckt. that daisy chains from one room to anothet?
See article section 700.12(F)

Roger
 