emergency exit signs in a church

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
Neighbor knocks on my door. His church needs exit signs and emer. lighting. So he's got the exit signs with the bug eye lights. There's 3 total. Questions: do they all have to be, on one dedicated emergency circuit? Or can I tap off a existing circuit somewhere? Can you use Romex in a church? I noticed in the attic they ran all EMT. Thank you for your help.
 

iwire

Moderator
Staff member
Location
Massachusetts
They go on the lighting circuit of the room they are to light.

I agree although there is an exception to that general rule.

Check out 700.12(E) or (F) for the rules.

Also a church is likely a place of assembly which rules NM out for the most part, I would use MC.
 

eprice

Senior Member
Location
Utah
Those areas 518.4(B) is addressing are those areas that are not places of assembly. Could be the offices of the chapel etc.

I don't agree. 518.4(B) says nothing about the spaces not being places of assembly. It only requires that the area not be required to be rated construction.
 

iwire

Moderator
Staff member
Location
Massachusetts
I don't agree. 518.4(B) says nothing about the spaces not being places of assembly. It only requires that the area not be required to be rated construction.


I do not think there is such a thing as a place of assembly that is not required to be fire rated.
 