When wiring an emergency generator, 700.10(D)(3) requires that the control wiring comply with 700.10(D)(1), this is also true for the generator feeder wiring.
700.10(D)(1) requires that the wiring be 2hr rated.
If the ATS is located in a 2hr rated room, 700.10(D)(2), and the generator is outside of the building, and the wiring is underground from the ATS in the 2hr rated room to the generator, does this wiring have to be 2hr rated?
Would the conduits to the emergency generator have to be 2hr rated or concrete encased, or because this is outside the building a 2hr rating is not required?
If a 2hr rating is not required because it is outside the building, is there a code reference?
Also, what’s up with the change in 700.1(D)(3) to monitor the control wiring?
Is that a generator manufacturer issue?
700.10(D)(1) requires that the wiring be 2hr rated.
If the ATS is located in a 2hr rated room, 700.10(D)(2), and the generator is outside of the building, and the wiring is underground from the ATS in the 2hr rated room to the generator, does this wiring have to be 2hr rated?
Would the conduits to the emergency generator have to be 2hr rated or concrete encased, or because this is outside the building a 2hr rating is not required?
If a 2hr rating is not required because it is outside the building, is there a code reference?
Also, what’s up with the change in 700.1(D)(3) to monitor the control wiring?
Is that a generator manufacturer issue?