Have 200kw 208v three phase 0.8 pf emeregency generator. Does NEC 2014 determine, guide or require sizing of the first emergency generator breaker size?

Sent from my SM-G935U using Tapatalk
 
Have 200kw 208v three phase 0.8 pf emeregency generator. Does NEC 2014 determine, guide or require sizing of the first emergency generator breaker size?

Sent from my SM-G935U using Tapatalk
Is this design issue or code?

Sent from my SM-G935U using Tapatalk
 
Is this design issue or code?

Sent from my SM-G935U using Tapatalk

There should be no difference from how you would size a feeder OCPD. You will need to consider a few things however:

1. The generator manufacturer will size the breaker that is integral to the unit, match it.
2. If NEC 700 or 701 system, you will need multiple breakers with separation.
 
Have 200kw 208v three phase 0.8 pf emeregency generator. Does NEC 2014 determine, guide or require sizing of the first emergency generator breaker size?

Sent from my SM-G935U using Tapatalk

Is it a health care facility? That could complicate things a bit since hospital generators are given some relief from the load calculations required by 220.

Otherwise, the only requirement would be that the breaker is sized for the load that needs to be supplied, and that the conductors the breaker supplies are sized per 300.
 