Hi All,
I'm trying to determine if a particular building requires an emergency generator. It is group B, less than 75 feet high, so, using the 2008 NYC building code (this is in brooklyn NY), i would follow chapter 27, section 2702.2.20 where it states:
"An emergency power system shall be required in those Group B, E, and R-1 occupancies specified in this section:
1. Group B occupancies with occupied floor less than 75 feet above the lowest fire department vehicle access having a gross floor area over 15,000 square feet per floor or a total gross floor area of 100,000 square feet or more."
The total square footage does not equal 100,000 square feet, so i am now obligated to follow the second condition... 15,000 square feet per floor. Is the code saying that every floor has to be over 15,000 sq. ft. for the building to require a generator, or that only one floor has to be over 15,000 sq ft (and the other floors can be less, like 10,000 sq ft)?
Thanks in advance!
I'm trying to determine if a particular building requires an emergency generator. It is group B, less than 75 feet high, so, using the 2008 NYC building code (this is in brooklyn NY), i would follow chapter 27, section 2702.2.20 where it states:
"An emergency power system shall be required in those Group B, E, and R-1 occupancies specified in this section:
1. Group B occupancies with occupied floor less than 75 feet above the lowest fire department vehicle access having a gross floor area over 15,000 square feet per floor or a total gross floor area of 100,000 square feet or more."
The total square footage does not equal 100,000 square feet, so i am now obligated to follow the second condition... 15,000 square feet per floor. Is the code saying that every floor has to be over 15,000 sq. ft. for the building to require a generator, or that only one floor has to be over 15,000 sq ft (and the other floors can be less, like 10,000 sq ft)?
Thanks in advance!