I have been assisting an engineering firm that does work in the data center field. They have an emergency generator 480V, 3760A, solidly grounded, and they indicated that the code does not allow them to have ground trip on the generator that trips but only to alarm. They refer to NEC 700.6(D) and 700.26 which uses the word 'indicate'.
The generator came with phase and ground overcurrent trips. There is no way to disable the ground trip without replacing the trip at a cost of $7000. Are they interpreting the code correctly?
To me it does not make since not to trip with the ground overcurrent function. Most likely the ground fault is going high enough that the phase overfunction is going to trip the breaker any way.