The emergency generator main breaker is located behind a locked door on the generator enclosure. The local AHJ would like a disconnect on the building because NEC, 701.11 paragraph B5. (providing "Readily Accessible Disconnecting means").
Note the exterior generator is 10' from the building.
And the Circuit breaker for an Emergency Systems Article 700 part VI Over protection 700.25 Accessibility.
The branch overcurrent devices for emergency circuits must be accessible to authorized persons only.
Also Article 700 700.12 General Requirements (B) (6) Outdoor Gensets.
what are the rules on this?
Note the exterior generator is 10' from the building.
And the Circuit breaker for an Emergency Systems Article 700 part VI Over protection 700.25 Accessibility.
The branch overcurrent devices for emergency circuits must be accessible to authorized persons only.
Also Article 700 700.12 General Requirements (B) (6) Outdoor Gensets.
what are the rules on this?