Hi all,
I'm trying to interpret something in the 2014 NYC Building Code. Section 2702.2.20. it states that low rise buildings (occupancy group B) need an emergency generator if the following is true:
"Group B occupancies with occupied floor less than 75 feet (22 860 mm) above the lowest fire department vehicle access having a gross floor area over 15,000 square feet (1393.6 m2) per floor or a total gross floor area of 100,000 square feet (9290.3 m2) or more."
The building I am looking at is less than 75 feet in height, and less than 100,000 sq. ft. gross floor area. So I have to look at the floor areas. 3 floors are greater than 15,000 sq.ft., but the 2 top floors are less than 15,000 sq.ft. Does this building require a generator?
I'm not sure if the code section is implying that each and every floor has to be 15,000 sq.ft., or if at least one floor is greater than 15,000 sq.ft., then you need the generator.
thanks!
I'm trying to interpret something in the 2014 NYC Building Code. Section 2702.2.20. it states that low rise buildings (occupancy group B) need an emergency generator if the following is true:
"Group B occupancies with occupied floor less than 75 feet (22 860 mm) above the lowest fire department vehicle access having a gross floor area over 15,000 square feet (1393.6 m2) per floor or a total gross floor area of 100,000 square feet (9290.3 m2) or more."
The building I am looking at is less than 75 feet in height, and less than 100,000 sq. ft. gross floor area. So I have to look at the floor areas. 3 floors are greater than 15,000 sq.ft., but the 2 top floors are less than 15,000 sq.ft. Does this building require a generator?
I'm not sure if the code section is implying that each and every floor has to be 15,000 sq.ft., or if at least one floor is greater than 15,000 sq.ft., then you need the generator.
thanks!