I don't have a copy of NFPA 110 handy, seems like it and NEC requires a means to shut down the prime mover- that could be a fuel shut off. There is also a UL standard for generators UL2200, might check it.
Here is the NEC
445.18 Disconnecting Means Required for Generators.
Generators shall be equipped with disconnect(s), lockable in the open position, by means of which the generator and all protective devices and control apparatus are able to be disconnected entirely from the circuits supplied by the generator except where both of the following conditions apply:
(1) The driving means for the generator can be readily shut down.
(2) The generator is not arranged to operate in parallel with another generator or other source of voltage.