My understanding is that if an emergency generator serves the emergency egress and exit lighting in a building, any "optional loads" that are connected to the same generator must be supplied from a separate automatic transfer switch. I believe this is what 700.5(D) states:
Am I missing something? Emergency exit and egress lighting are Article 700 loads, correct? If I am correct, hasn't this been in the code for a very long time?
Doing remodel designs, almost every generator I run across serves em lighting and other loads from the same transfer switch. The other loads on the same ATS are often the boiler and circulation pumps.
It's getting old telling clients their existing generator doesn't meet code, and they should either install unit equipment with battery backup, or install another ATS.
Code:
NEC 700.5(D) - Transfer equipment shall supply only emergency loads.
Am I missing something? Emergency exit and egress lighting are Article 700 loads, correct? If I am correct, hasn't this been in the code for a very long time?
Doing remodel designs, almost every generator I run across serves em lighting and other loads from the same transfer switch. The other loads on the same ATS are often the boiler and circulation pumps.
It's getting old telling clients their existing generator doesn't meet code, and they should either install unit equipment with battery backup, or install another ATS.