There have been several threads on emergency lighting lately. I have a question regarding relative costs between the two main alternatives of providing emergency lighting power ? batteries vs generator.
Alt #1: Vanilla battery packs, bug eyes, exit signs, fluorescent with battery back-up, etc. This has the big advantage of lowest installed cost and simplicity.
Alt #2: Building has an emergency generator to maintain critical computer, process, etc. systems. From what I see Art 700 (life safety) requires 10 second start, independent transfer switch, dedicated conduits, ID of all boxes and enclosures, etc. Does this ?identification? include junction boxes, LB's, etc? What about the fixtures themselves? One now has a potentially large amount of dedicated emergency conduits running all over the building with a significant first cost plus the second transfer switch, an emergency panelboard, etc. One does offset these costs by not having to buy battery units.
Note, even when a building does NOT need a generator, does a generator for emergency lighting ever ?pay off?? You have to consider the maintenance costs of having a generator vs battery packs. While there are costs of replacing battery packs or their batteries at some point, a generator does have a significant maintenance cost as well.
Obviously, higher buildings will have a generator for the elevator, if nothing else.
I see the cost for Alt #2 as very high and generally the client will balk.
Often the egress emergency lighting is on 24/7. My experience has been these lamps go first and seldom are replaced in a "timely manner." There is a "transfer device" that can be installed in fixtures that allows the fixtures to be switched on and off via the normal power circuit but transfers to emergency source when normal power fails and turns the lights on. But, how will the AHJ take to these? Plus, they are yet another additional cost.
How do you see the overall cost difference between the two alternates falling out? Obviously, a very large building would likely be cost effective with the generator. I am really concerned with small and medium sized buildings.
Any thoughts on this issue will be appreciated!
RC
Alt #1: Vanilla battery packs, bug eyes, exit signs, fluorescent with battery back-up, etc. This has the big advantage of lowest installed cost and simplicity.
Alt #2: Building has an emergency generator to maintain critical computer, process, etc. systems. From what I see Art 700 (life safety) requires 10 second start, independent transfer switch, dedicated conduits, ID of all boxes and enclosures, etc. Does this ?identification? include junction boxes, LB's, etc? What about the fixtures themselves? One now has a potentially large amount of dedicated emergency conduits running all over the building with a significant first cost plus the second transfer switch, an emergency panelboard, etc. One does offset these costs by not having to buy battery units.
Note, even when a building does NOT need a generator, does a generator for emergency lighting ever ?pay off?? You have to consider the maintenance costs of having a generator vs battery packs. While there are costs of replacing battery packs or their batteries at some point, a generator does have a significant maintenance cost as well.
Obviously, higher buildings will have a generator for the elevator, if nothing else.
I see the cost for Alt #2 as very high and generally the client will balk.
Often the egress emergency lighting is on 24/7. My experience has been these lamps go first and seldom are replaced in a "timely manner." There is a "transfer device" that can be installed in fixtures that allows the fixtures to be switched on and off via the normal power circuit but transfers to emergency source when normal power fails and turns the lights on. But, how will the AHJ take to these? Plus, they are yet another additional cost.
How do you see the overall cost difference between the two alternates falling out? Obviously, a very large building would likely be cost effective with the generator. I am really concerned with small and medium sized buildings.
Any thoughts on this issue will be appreciated!
RC