I have an existing building with an existing generator that only supports an ATS serving an emergency panel w/ NEC 700 emergency fixtures. The generator is being replaced with a larger one to back up the entirety of the service. Rather than provide a generator with two output breakers would it be acceptable to remove the emergency lighting circuits from the existing emergency panel and run them through an appropriate UPS or inverter? I know that the UPS would always see normal power since the generator is backing up the normal source, is this problematic? Is there such a thing as a UPS that can interlock with a generator in a way that the UPS would remain on until the signal from the generator is removed. I'm just trying to find a workaround that could save us the cost of a generator with an additional load breaker, two disconnects, and one transformer.