reskra said:
Can anyone tell me if emergency lighting in classrooms is a code requirement?:smile:

Really, the answer to this comes from the building code, not the NEC. The answer typically depends things such as occupant load ect..

Best to check with your local building department.

Chris
 

muskiedog

Senior Member
Location
Minnesota
NFPA 101 Life SAfety code will direct you on this

NFPA 101 Life SAfety code will direct you on this

Most likely not. Now the means of egress will need to be but most likely not the classroom.
 

barbeer

Senior Member
According to NFPA 101-14.2.9 classrooms w/o windows require EM lighting.

Florida Building Code (which supercedes NFPA 101) 423.17.1 says EM lighting shall be provided in student occupied areas. (classrooms)

Generally (here at least) local code officials do not review plans or inspect buildings of a public school, they are built to stringent specifications and inspected by school board inspectors. In my experience they all have EM lighting everywhere.
 

reskra

Member
Emergency lighting in classrooms

I can't seem to find the specific verbage in NFPA 14.2.9. It refers us to 7.9 which doesn't specifically mention classrooms.
 

reskra

Member
I can't find specific verbage about classrooms w/o windows in NFPA101 14.2.9 but it does refer me to NFPA101 7.9, and this too does not specifically mention classrooms w/o windows.
 

dlhoule

Senior Member
Location
Michigan
I agree with Raider 1, check with local building dept.

In one of the industrial facilities I do work for, they have class rooms some with and some without emergency lighting. As far as I can tell they are not required. These class rooms also have no windows.
 

cadpoint

Senior Member
Location
Durham, NC
Thats kinda tricky having a "classroom" in an industrial. Theres specific rules that deal with assembly and egress one would need to followed, over riding the class of structure or various types of structure in one edifice, and others have posted on it. :rolleyes:. Office space adjoining Industrial space comes to mind. But it all comes down to, also said, the AHJ, how they apply the NEC and their building codes.

A good set of drawing will not cause any questions to be asked in the
field. Toast someone when get a set!
 