Emergency Lighting in parking garages

Merry Christmas
Status
Not open for further replies.

MGE

Member
Location
San Diego Cal.
Does anyone know if "E" Lighting is required for underground parking garages with 2 levels. The North side has 4' 2-lamp strips with a regular ballast and is not fed from the backup generator.

The South side has 8' 4-lamp strip fixtures and has a regular 2-lamp ballast AND a 2-lamp "E" ballast. these lights are not fed from the backup generator also.

This is in San Diego Cal. Thanx MGE
 
I think at some emergency lights would be in order. If the power went out,it could easily become pitchblack. I dont know if they would be required. You should check with the building inspector
 
LSC - 42.8.2.9 - Parking structures shall be provided with em. lighting, except for structures occupied only during daylight hours that meet natural light reqs.

7.9.1.1 (2) - Emergency lighting shall be provided for the following: Underground and limited access structures.

I have no idea if California has any specific rules about this but I would believe it to be required.
 