Does any know if Emergency Lighting Inverter Systems (UL924 Battery System) are required to be installed in 2-hour rated room? I know per NFPA-110 7.2.1.1 that a generator and transfer equipment used for emergency power (like egress lighting) need to be installed in a 2-hour rated room. I've designed and installed many systems and have never heard or seen this requirement for UL924 Emergency Lighting Inverter Systems. I've always understood that Emergency Lighting Inverter Systems would fall under NFPA-111 "Standard on Stored Electrical Energy Emergency and Standby Power Systems" and not the NFPA 110 "Standard for Emergency and Standby Power Systems". NFPA-111 doesn't have the same 2-hour rated room requirement. The NFPA 101 Life Safety Code Section 7.9.2.4 states "Emergency generators and related transfer switch equipment that provide power to emergency lighting systems shall be installed, inspected, tested, and maintained in accordance with NFPA 110. Stored electrical energy systems, where required in this Code, other than battery systems for emergency luminaires in accordance with 7.9.2.5, shall be installed, inspected, tested, and maintained in accordance with NFPA 111."
All I received was a vague comment "2016 NFPA sections addressed that Automatic Transfer Switches, Lighting Inverters and emergency distribution equipment be placed in 2 hour fire rated rooms." Without any guidance to specific NFPA Publication or Section.
All I received was a vague comment "2016 NFPA sections addressed that Automatic Transfer Switches, Lighting Inverters and emergency distribution equipment be placed in 2 hour fire rated rooms." Without any guidance to specific NFPA Publication or Section.