dpm457
Member
- Location
- Denver, CO
Recently my company hired contractors for a large-scale LED retrofit project (6000+ lamps). They are all 3 lamp T8 2x4 fixtures. The "plan" for the EM fixtures was to wire line voltage (277v) to the two outside tombstones for the LED lamps and then use a normal and EM ballast with a Fluorescent T8 lamp on the center pair of tombstones. This probably isn't the best method but my company wanted to save cash. Now- after 4 months of performing my OSHA required monthly 30 second test, all of the fixtures passed the test. Keep in mind that I was only using the test button for these inspections. During a scheduled building shut-down I decided to conduct the annual 90 minute inspection and a vast majority of the EM fixtures did not even attempt to turn on- just dark. Because it wasn't a 100% fail rate, I know this set-up works. However, I cannot determine the difference in the wiring between the working fixtures and the failed ones. So my question is: Why would the EM ballast and lamp operate while using the test button but not on a total loss of power?
Signed,
So Confused!