I see a guy installing emergency lighting (the small battery back up type) and he tapped into a duplex receptacle circuit and not the normal lighting cicuit!! I thought maybe there may be an exception for him somewhere but its just not there!! 2008 NEC 700.17 IS very clear.
Even if it was an exception, this would be a bad design. You want the battery light to come on when the lights go out!!. Correct me if Im wrong or missing something in the code.