Emergency Lighting on Standby Generator

Status
Not open for further replies.

dav5y

Member
Location
NYC
Hi All

I'm curious if emergency lighting fixtures need to have battery back-up in addition to being connected to the emergency generator ???? The generator ATS is set to transfer at 8 seconds, if that helps in the answer....
 

mgookin

Senior Member
Location
Fort Myers, FL
I always understood means of egress illumination required to be lit within 10 seconds under the building code if powered by emergency generator. I think you're ok, but check with your fire marshal to make sure you don't step on anyone's toes.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Hi All

I'm curious if emergency lighting fixtures need to have battery back-up in addition to being connected to the emergency generator ???? The generator ATS is set to transfer at 8 seconds, if that helps in the answer....

If your "emergency generator" is a compliant Article 700 system, then no. If your generator is actually an Optional Standby Art. 702 system, then yes, as this from a code standpoint is not an emergency system.
 