With National Fire Safety Week coming up in October, I'd like a refresher on testing light units.
Bob O.84,Pa.
Bob O.84,Pa.
muskiedog said:NFPA 101 31-1.3.8 Periodic Testing of Emergency Lighting Equipment states: A functional test shall be conducted on every required emergency lighting system at 30-day intervals for a minimum of 30 seconds. An annual test shall be conducted for the 1 ?-hour duration. Equipment shall be fully operational for the duration of the test. Written records of testing shall be kept by the owner for inspection by the authority having jurisdiction.
OSHA 29 CFR.1910.36 (d)(2) states: ?Every automatic sprinkler system, fire detection and alarm system, exit lighting, fire door, and other item of equipment, where provided, shall be continuously in proper operating condition.?
muskiedog said:I have been doing it for about twenty years. It is one of my number on gigs though when I do my facility inspections. No one needs them till the power is out.