I want to introduce myself as a new member to the forum. This is my first question to this site.

I have a 277 volt 3 KVA 30 amp breaker feed emergency lighting power ups that is located in a area that is cooking the batteries.

The new cooler location is 100 feet away from the above location.

There is a relay/ fused distribuition box that # 10s outputs go to 3 # 12 with 20 amp KTK fusing by the existing location to 3 floors.

There is a disconnect switch built into the unit 2-pole

Can the power 30 amp supply and output be in the same conduit from the UPS new location to the relay/fused distribuition box?

Thanks in advance!
MH1990
 
Article 700.9(B) prevents normal and emergency wiring in the same raceway.There are some exceptions at the point of supply and at the equipment itself.
Welcome to the forum!