Good afternoon,
We conducted a site visit at a large building that is equipped with two services. One service (Service #1) is effectively 2000A @ 480/3. The other service, (Service #2) is approximately 150A @ 480/3. Service #2 is backed up with a ATS and 75 kW generator.
The whole purpose of this service #2 is to feed lights throughout the building which are lit 24/7, and are NOT equipped with any switches. Basically, the lights are always on, and if the power goes out, the generator will start (Hopefully after 10 seconds) and these lights will continue to be illuminated. This generator also feeds a couple other items such as a large IT closet.
Does anyone see any issues with this installation assuming that all areas that require emergency lights have a fixture? Keep in mind, this was built under the NEC 1990.
I see a couple problems but not sure how it relates to codes
#1. The lights burn all the time, and most of them were burnt out.
#2. It takes 10-15 seconds for a good ATS to start depending on different conditions.
#3. There is no redundancy to this system. If the generator fails, none of the lights will come on. Typically, even if 20% of typical battery backup fixtures fail, you can still make your way out of the building.
Thanks!
We conducted a site visit at a large building that is equipped with two services. One service (Service #1) is effectively 2000A @ 480/3. The other service, (Service #2) is approximately 150A @ 480/3. Service #2 is backed up with a ATS and 75 kW generator.
The whole purpose of this service #2 is to feed lights throughout the building which are lit 24/7, and are NOT equipped with any switches. Basically, the lights are always on, and if the power goes out, the generator will start (Hopefully after 10 seconds) and these lights will continue to be illuminated. This generator also feeds a couple other items such as a large IT closet.
Does anyone see any issues with this installation assuming that all areas that require emergency lights have a fixture? Keep in mind, this was built under the NEC 1990.
I see a couple problems but not sure how it relates to codes
#1. The lights burn all the time, and most of them were burnt out.
#2. It takes 10-15 seconds for a good ATS to start depending on different conditions.
#3. There is no redundancy to this system. If the generator fails, none of the lights will come on. Typically, even if 20% of typical battery backup fixtures fail, you can still make your way out of the building.
Thanks!