Can you wire light fixtures containing emergency ballast through a lighting contactor? The control circuit for the contactor may trip and the lights go out leaving everyone in darkness. The emergency ballast are not wired to the control circuit but are wired ahead of the contactor to the circuit feeding the light.
 

iwire

Moderator
Staff member
Location
Massachusetts
Can you wire light fixtures containing emergency ballast through a lighting contactor? The control circuit for the contactor may trip and the lights go out leaving everyone in darkness. The emergency ballast are not wired to the control circuit but are wired ahead of the contactor to the circuit feeding the light.

We do it all the time but use normally closed contactors so a circuit or coil failure leaves the lights on not off.
 