U know the ones that u typically see in hallways and stairwells, with the batter backup. Do they need to be on their own, or can they be combined with general lighting branch circuits? Thanks.
2002 NEC
700.12 General Requirements.
(E) Unit Equipment.
Unit equipment shall be permanently fixed in place (i.e., not portable) and shall have all wiring to each unit installed in accordance with the requirements of any of the wiring methods in Chapter 3. Flexible cord-and-plug connection shall be permitted, provided that the cord does not exceed 900 mm (3 ft) in length. The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches. The branch circuit that feeds unit equipment shall be clearly identified at the distribution panel. Emergency luminaires (illumination fixtures) that obtain power from a unit equipment and are not part of the unit equipment shall be wired to the unit equipment as required by 700.9 and by one of the wiring methods of Chapter 3.
Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature.
Bonding Jumper, The wire is not so much a sensing wire as a constant feed to charge the battery and power the lamps, the wire that runs from the switch is more of a control wire.Originally posted by bonding jumper:
Another question, does a sensing wire used for the emergency flourescents that I referred to before need to be #12 or can they use a small wire.
I believe the answere to that question is found in the applicable building code. In the IBC, look at section 1003.2.11.Originally posted by bonding jumper:
...What rooms require emergency lighting? Talking apartment complex, i would say off hand = lobbys, hallways, community rooms. But how about utility rooms, and rooms used for storage of supplies and such?...
Well, that depends on the building code in effect. In the IBC, the requirement for emergency lighting kicks in if the room or corridor in question requires two or more exits as determined by other sections of the code. In the UBC it kicks in if the area in question serves an occupant load of 100 or more, as determined by other sections of the code.Originally posted by muskiedog:
Appropriate illumination must be provided for public spaces, hallways, stairways and other egresses. Your utility rooms probably will not require such lighting but if there are laundry rooms or spaces used by the general public it should then have emergency lights.