I am currently working on the design of a retail space that will have an emergency lighting panel fed from a Mall provided emergency panel that has power back up via a generator. My question is this:
Is it possible to have emergency lighting circuits composed of lighting fixtures that are ON all the time and some that have battery back up and OFF all the time except when normal line power is lost wired together or seperately but coming off of the emergency panel? If so, how can this be accomplished in terms of wiring and code compliance?
Pete I truly am not being rude but I know these guys work hard and come home tired and this sentence about lights is hateful on an old tired mind...
Why don't you add some commas or something and explain the issue a little better. Because I need to go lay down after looking at it
Anyway check this out for e-lighting circuits
700.17 Circuits for Emergency Lighting. Branch circuits
that supply emergency lighting shall be installed to provide
service from a source complying with 700.12 when the
normal supply for lighting is interrupted. Such installations
shall provide either of the following:
(1) An emergency lighting supply, independent of the general
lighting supply, with provisions for automatically
transferring the emergency lights upon the event of
failure of the general lighting system supply
(2) Two or more separate and complete systems with independent
power supply, each system providing sufficient
current for emergency lighting purposes
Unless both systems are used for regular lighting purposes
and are both kept lighted, means shall be provided
for automatically energizing either system upon failure of
the other. Either or both systems shall be permitted to be a
part of the general lighting system of the protected occupancy
if circuits supplying lights for emergency illumination
are installed in accordance with other sections of this
article