Read 700.12(F) for unit equipment it must be on the same circuit in the room unless there are 3 or more circuits of lighting. If you have a non "unit equipment" installation, they could be on a separate circuit, but you need to comply with 700.16 so the failure of any one lamp cannot leave in total darkness any space that requires emergency illumination.