Is emergency lighting require in electrical rooms with equipment over 1200volts
R rocco5303 New member Jul 23, 2010 #1 Is emergency lighting require in electrical rooms with equipment over 1200volts
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 23, 2010 #2 Illumination is required per 110.26(D), whether or not emergency lighting is required would be a local building code issue. Roger
Illumination is required per 110.26(D), whether or not emergency lighting is required would be a local building code issue. Roger