I was recently asked to add some devices to an existing emergency generator in a new parking garage for a client of mine. The new garage was completed in 2007. The garage has a 150 KW generator with tranfer switch and emergency distribution panelboard. During my evaluation I found that there was no seperation between the emergency system and the normal power. All of the lighting and power were run throughout the building in the same conduit system. There was also a trough installed in the electric room that basically intertwined the branch circuits and the feeders with no seperation or designation. Also. the entire parking area had HID lighting with not one restrike throughout the entire 10 floors. Is there some exception to the code I am not seeing? I thought the systems must be kept seperate except as defined by the code in section 700.9 (B). When the contractor was questioned the response back was that they were granted an exception by the city because the building was leased??? Can anyone shed a little light on this?