barkett519
Member
- Location
- MA
- Occupation
- Journeyman Electrician
Hi all,
I was talking with my boss the other day...we were having a heated discussion, im hoping you guys can shed some light for me? It was regarding the new 2020 requirement for an emergency disconnect outside of a dwelling. I told him I am 90% sure you have to bond the egc, gec and the neutral in the disconnect outside and run a 4 wire ser cable into the house and separate the grounds and neutrals. He says a 3 wire cable is acceptable run to the inside and the egc and neutral do not have to be bonded in the outside disconnect, they can still be bonded in the main panel( providing the main panel has a main breaker of course) can someone please explain? I've read the code and from what I understand neutrals and grounds have to be bonded at the first service disconnect. Isn't that the outdoor emergency disconnect?
I was talking with my boss the other day...we were having a heated discussion, im hoping you guys can shed some light for me? It was regarding the new 2020 requirement for an emergency disconnect outside of a dwelling. I told him I am 90% sure you have to bond the egc, gec and the neutral in the disconnect outside and run a 4 wire ser cable into the house and separate the grounds and neutrals. He says a 3 wire cable is acceptable run to the inside and the egc and neutral do not have to be bonded in the outside disconnect, they can still be bonded in the main panel( providing the main panel has a main breaker of course) can someone please explain? I've read the code and from what I understand neutrals and grounds have to be bonded at the first service disconnect. Isn't that the outdoor emergency disconnect?