I understand I had similar post perviously but that post involve GFPE of main service switchboard.
See attached sketch. I have high rise in which their is main service switchboard, emergency gen, ATSs one emergency life and safety and another standby. Switchboard 250A feeder breaker feeds ATS emergency branch. Generfator has 250A main breaker feeding ATS emergency
Emergency ATS feeds emergency panelboard 250A main breaker with LSIG.
Its confusing in this case NEC 2017 section 700.6(D) to indicate a ground fault but not have ground fault protection.
Does NEC 2017 section 700.6(D), 700.31 or any another NEC 2017 article allow ground fault protection breaker in emeregency breaker panelboard with 250A main breaker attach sketch or not?
See attached sketch. I have high rise in which their is main service switchboard, emergency gen, ATSs one emergency life and safety and another standby. Switchboard 250A feeder breaker feeds ATS emergency branch. Generfator has 250A main breaker feeding ATS emergency
Emergency ATS feeds emergency panelboard 250A main breaker with LSIG.
Its confusing in this case NEC 2017 section 700.6(D) to indicate a ground fault but not have ground fault protection.
Does NEC 2017 section 700.6(D), 700.31 or any another NEC 2017 article allow ground fault protection breaker in emeregency breaker panelboard with 250A main breaker attach sketch or not?