• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Emergency Power and Standard Power in the same conduit...

Status
Not open for further replies.
Location
06074
Occupation
Electrical Engineer
Emergency Power;

We have back up generators that come on automatic when we loose power, this EPower takes care of most emergency lighting and door controls and emergency
lighting. Can non emergency cabling be used in the same conduit as emergency power connected devices? If not what code or requirement would cover this
type installation?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is this really an Article 700 application? Did an AHJ require this? Please review scope of Article 700, 701 and 702.
Many users call any generator an Emergency Generator
Can you update your profile with your location?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The wiring has to be kept separate from all other wiring. See 700.10(B).
A few years ago there was a fire in a cable duct at the Bellagio Resort in Vegas. They ran the cables from the utility feed and the backup generator in the same duct. The resort and casino was down for almost a week. I can’t imagine what kind of revenue loss that represented for them, but is was going to be a LOT more than the cost of running a second duct.


Looks like it was $3 million /day.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Is this really an Article 700 application? Did an AHJ require this? Please review scope of Article 700, 701 and 702.
Many users call any generator an Emergency Generator
Can you update your profile with your location?
But the OP stated that the generator fed the emergency lighting. In order to use the generator to feed emergency lighting, (as its secondary power source) it would HAVE to be and comply with article 700.
 
Status
Not open for further replies.
Top