snace
Member
- Location
- Allentown, PA USA
Background
I am working on a renovation of a Sewage Pump Station were we upgraded the existing pumps and associated controls, but reused the existing service and generator. I have two new 75HP pumps with motors and a new control panel; by others. The control panel has individual starters (Siemens Sirius) with 150A CB's for each motor and the starters were programmed to limit the inrush. During testing, we found the starters would trip out and fail to across the line from poor power quality. We found that the pump station was at the end of a long utility feed and had voltage drop and poor power quality from local industrial loads. We installed a new utility pad mount transformer to improve the power quality and everything has been working great for a few months under normal or emergecny power.
Recently, the pump station was tested under emergency power and the starters are back to doing the same thing (but only under emergency loads). We are going to have the generator load bank tested to see if something has changed from a power quality standpoint.
Has anyone experienced this same issue with a genertor causing soft starters to trip out? Any suggestions as to what else could be happening? Thanks.
I am working on a renovation of a Sewage Pump Station were we upgraded the existing pumps and associated controls, but reused the existing service and generator. I have two new 75HP pumps with motors and a new control panel; by others. The control panel has individual starters (Siemens Sirius) with 150A CB's for each motor and the starters were programmed to limit the inrush. During testing, we found the starters would trip out and fail to across the line from poor power quality. We found that the pump station was at the end of a long utility feed and had voltage drop and poor power quality from local industrial loads. We installed a new utility pad mount transformer to improve the power quality and everything has been working great for a few months under normal or emergecny power.
Recently, the pump station was tested under emergency power and the starters are back to doing the same thing (but only under emergency loads). We are going to have the generator load bank tested to see if something has changed from a power quality standpoint.
Has anyone experienced this same issue with a genertor causing soft starters to trip out? Any suggestions as to what else could be happening? Thanks.