I have a customer with an existing generator that is Wye connected to provide 240/139 3ph4w or 480/277 3ph4w. The existing service which includes a manual transfer switch is 240/120 3ph4w. What I propose I have never seen done before so I thought I would see if anyone has had any experience with this situation. What I would like to do is install a 75KVA 480-240/120 3ph4w transformer to be supplied from the 480v of the generator. The 3-phase load for this batch plant consist of only (3) 7-1/2hp 240V motors and some 120V loads associated with scales and some lighting. Under normal conditions I would keep the three-phase and single-phase separated and it is after the manual transfer switch. I do not want to install three separate transformers as this is only for emergency power that will be seldom used and then only for short periods of time. My thought is, that by over sizing the transformer I am basically treating it as a single-phase transformer with respect to the 120V loads and allowing a reduced three-phase load so as not to over-load the single-phase winding. I estimate the motors will total about 9300va per phase and that would leave a additional 7200va per single-phase winding or 14,400 @240V 1ph which is allowing for as much as 60amps of 120V loads. Since the three-phase loads are known and the single-phase loads are estimated to be not over 40amps this seems to allow some safety factor in the loading. I plan on protecting the secondary with a 150Amp breaker which is 30amps under the max available line-amps. Looking this over I figure the three-phase coil amps to be about 38.75 and the singl-phase coil amps to be about 98.75 which is below the max coil amps of 104. I would be interested on anyone input and especially hearing from anyone who has had experience with such an installation.