Emergency power in same room

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
1) Is it permitted to have article 517, life safety or legally required standby in the same switch gear as the main power?

2) Can an emergency generator be in the same room as the main switch gear?

3) Can ATS, emergency gear ect be in the same room as the main switch gear or MV transformer?

If not what year did these go into effect? And if not what NFPA article am I looking at in terms of fire protection? What other requirements?
 

Attachments

  • gen 1.jpg
    gen 1.jpg
    93.7 KB · Views: 5
Nothing explicit on separation though.

There has to be something, I can't imagine the generator feeding into the same gear as the POCO.

maybe this ditty in the info note??:?

and is arranged to
provide mechanical and electrical separation so that a fault
between the facility and the generating sources is not likely to
cause an interruption of more than one of the facility service
feeders.

~RJ~
 