Frederick Cox
Member
A normal-power 480V switchboard originally direct-fed a 600 amp transformer load. An emergency power source was later introduced to feed this transformer, via a properly-installed 600/3 ATS. However, the original feeder cable was intercepted in the switchboard and extended to the ATS as the normal-source feed, and the load feeder out of the ATS (now = emergency power) re-entered the switchboard where it was spliced into the original transformer feeder. Thus, emergency power is running through the normal-power switchboard. Workmanship and materials appear good; just the decision to do it this way is in question.
Is it sufficient to wrap the emergency cable with Scotch 77 fire tape and affix tags & labels describing the external emergency power source? Or must these emergency cables be completely removed from the switchboard? Thank you!
Is it sufficient to wrap the emergency cable with Scotch 77 fire tape and affix tags & labels describing the external emergency power source? Or must these emergency cables be completely removed from the switchboard? Thank you!