Can feeders for an emergency system be routed through an optional standby panel. I was thinking that you can based on 700.9 B, but the engineer is saying that you can't. Any help is appreciated.
 
Which of the five sub-paragraphs of 700.9(B) are you planning to use, as your basis for calling this acceptable? I don't see any that would apply. So I agree with the engineer.
 
I agree with the engineer, Charlie, and Pierre.

BTW, it's nice to see you back Pierre.