Emergency Shower GFCI

Status
Not open for further replies.

MFinch97

Member
Location
Colorado
Occupation
Commercial Electrician
I would like to get your take on emergency eye wash stations and GFCI requirements. I had an Inspector call it a shower stall and required GFCI within 6 feet. My argument of it being a dry location because of it only being temporarily wet did not sway their mind. Is there anything that may come to mind regarding any requirements per NFPA 70?
 
I have to agree with the inspector. It doesn't matter how often it is used... The code doesn't make that distinction
 
There are no mentions of "eye wash" stations in the NEC. IMHO you would have to treat it like a sink in which case all receptacles within six feet would have to be GFCI. I also think that you would want to make sure that the GFCI is not being deluged with water when the eye wash is being operated i.e. the GFCI is not placed under the station.
 
I would put an in-use cover on that. One of the flat ones that would not interfere with a head. Or better yet, relocate the receptacle. BTW, I have seen those stations used frequently by people who wanted to wash their hands. I have also seen new men coming onto a job test them to make sure they are working.
 
Definition of sink (Entry 2 of 2)
1a: a pool or pit for the deposit of waste or sewage : CESSPOOL
b: a ditch or tunnel for carrying off sewage : SEWER
c: a stationary basin connected with a drain and usually a water supply for washing and drainage

I think it probably qualifies as a sink. I think the receptacle needs GFCI protection.

I don't see how it is a shower stall. It might be a shower but not a shower stall.

Best bet is to move the receptacle.

I do not think it is a wet location.

Location, Wet. Installations underground or in concrete slabs
or masonry in direct contact with the earth; in locations subject
to saturation with water or other liquids, such as vehicle washing
areas; and in unprotected locations exposed to weather.

I don't see how getting some splashing on it from the eyewash station makes it "subject to saturation with water". If mere splashing was the criteria, than every receptacle would be in a wet location. Someone could walk by and spill coffee on it.
 
Dang it I thought there were the new urinals with a bidet. They really should put a sign up to let people know it's an eye wash station.
 
Thread title is “Emergency Shower...” but the discussion is about eye wash stations. They are not the same thing.

GFCI would be required in either case, I think.
 
When I was an undergrad I spent lots of time in the chem lab. There were emergency showers everywhere. No stall, just a shower head with a pull chain. Sometimes they were even over a floor drain.

If you pulled the chain, everything in the vicinity would get wet. Walls, floor, desks, book shelves.....

-Jon
 
I would like to get your take on emergency eye wash stations and GFCI requirements. I had an Inspector call it a shower stall and required GFCI within 6 feet. My argument of it being a dry location because of it only being temporarily wet did not sway their mind. Is there anything that may come to mind regarding any requirements per NFPA 70?
Let me clarify, this was an emergency eye wash/shower. No drain basin or anything to make it a stall in my eyes. Also The NEC does in fact clarify what a dry location is. The definition of a dry loaction is: A location not normally subject to dampness or wetness. A location classified as dry may be temporarily subject to dampness or wetness, as in the case of a building under construction.
 
I would like to get your take on emergency eye wash stations and GFCI requirements. I had an Inspector call it a shower stall and required GFCI within 6 feet. My argument of it being a dry location because of it only being temporarily wet did not sway their mind. Is there anything that may come to mind regarding any requirements per NFPA 70?
They had drains below them, just no Basin.
 
I think it probably qualifies as a sink. I think the receptacle needs GFCI protection.

I don't see how it is a shower stall. It might be a shower but not a shower stall.

Best bet is to move the receptacle.

I do not think it is a wet location.



I don't see how getting some splashing on it from the eyewash station makes it "subject to saturation with water". If mere splashing was the criteria, than every receptacle would be in a wet location. Someone could walk by and spill coffee on it.
They was no connection for a drain, but there was one on the ground. I would think with that it does not qualify as a sink.
 