Emergency stops

Status
Not open for further replies.

adam_p

New member
Is it required for a "reset" to be pressed after an "E-stop" has been depressed. We have several pieces of equipment that actually use the red mushroom-head style switches for on/off control. I thought this was against OSHA regulations for equipment to automatically restart just by pulling the button out again.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: Emergency stops

It depends.

If you are referring to a machine covered under NFPA79, and this is truely an emergency stop as defined there, this is indeed a requirement.

[ September 23, 2005, 05:12 PM: Message edited by: petersonra ]
 