I would like to consider the use an emergency system common bus to supply an emergency system (100A) and optional stand-by systems (400A) with automatic selective load pickup and shedding on an existing 200 kW/250 kVA, 480/277 V generator (no room to replace with larger generator). However, 445.13(A) requires all feeders to be 115% of generator nameplate current rating. A #500 feeder for the 100A emergency system makes the common bus approach impractical. 445.13(B) allows a tap IAW 240.21(B) which appears to be shown in Exhibit 700.3 (single feeder that supplies multiple ATS). However, a common OCPD isn't really practical with automatic selective load pickup and shedding because the common OCPD doesn't need to be larger than the optional stand-by system OCPD (400A) and it would be better to avoid upstream OCPD when possible with an emergency system. Am I missing something in regards to 700 and 445.13? Do you have any recommendations in regards to providing Common OCPD or not?