Question regarding Electrical Emergency Generator sizing.
I have a 600A service, existing peak demand 115A @208V 3Ø
Theres an existing 80KW generator (Max 278A @208V 3Ø output with .8 power factor).
My new added loads plus existing peak is 350A. Typically i would just size the generator to be above demand, but i dont want to force the client to pay an additional $70K if the existing may support the load of real world demand. Is there a code requirement that requires you to size based on demand or how would one go about stating the existing gen set very well could support the loads after construction without requiring a oversizing the generator?
Thanks,
I have a 600A service, existing peak demand 115A @208V 3Ø
Theres an existing 80KW generator (Max 278A @208V 3Ø output with .8 power factor).
My new added loads plus existing peak is 350A. Typically i would just size the generator to be above demand, but i dont want to force the client to pay an additional $70K if the existing may support the load of real world demand. Is there a code requirement that requires you to size based on demand or how would one go about stating the existing gen set very well could support the loads after construction without requiring a oversizing the generator?