Emergency Wiring Interpretation

Status
Not open for further replies.

scotteng

Member
Location
Apollo Beach, FL
Occupation
Professional Engineer
Please forgive the length in advance, but the issue deserves it to fully explain my dilemma...

I have designed a 14,300 sq. ft. grocery store which is one tenant within a larger retail building. This is phase I of the project. In phase III, the store will take over an adjacent tenant and become closer to 40,000 sq. ft. A generator was initially planned to be part of phase III. Thus, without a generator in phase I, our design used battery packs (unit equipment) for the emergency lighting. The batteries are in the fixtures, not wall mounted emergency lights.

A couple of days before the permit for phase I is due, the owner decides he would like the generator in phase I.

Because the store was designed with battery packs, it was agreed that we would leave the wiring and batteries as-is and treat the generator as optional stand-by. The owner wanted their lights to continue to run as the primary function of the generator, so we installed the transfer switch ahead of the lighting panel. Thus, if utility drops out, the unit equipment powers the emergency lights for 10 seconds until the stand-by generator kicks in and all lights come on. The store would then still have 90 minutes of emergency lighting in the event the generator failed as well.

During plan review, the reviewer states that in the City of Los Angeles, you cannot connect an optional stand-by generator to the normal power system and it subsequently feed fixtures with unit equipment. There is no requirement stating such that I can find in the Los Angeles Municipal Code (a.k.a. local amendment), California Electrical Code (derivation of the NEC), or the California Building Code (derivation of the IBC).

Some of his statements are:
? The wiring design is acceptable if we remove the generator (and thus don't have a second normal source powering emergency fixtures).
? That design is acceptable if we re-circuit the emergency fixtures to a panel that is not fed from the generator.
? His interpretation is that 700.12, unit equipment normal source means "utility source".

I asked to speak to the head electrical plans reviewer for LADBS, and to my amazement, his response was the same. "You can't do that here". He said "once you put in a generator and connect it to your emergency lights, that generator is an emergency generator and all wiring will be considered emergency wiring if they power emergency lights". Neither understood that our emergency wiring in the store is only the leads coming out of the battery ballast. Neither would take the time to clearly state a code section that backs their "interpretation" other than to state that the portion of 700.12 for unit equipment that talks about the "normal" source, they define that as being the utility company.

Admittedly, I am hard headed, but I've designed literally hundreds of stand-by and emergency generator systems and feel I have a rock solid understanding of each. If there is anyone who can help with a convincing argument I could use, I would greatly appreciate it.
 
Admittedly I'm kind of rusty on Articles 700, 701 and 702 but it doesn't seem logical if you already satisfied the emergency egress issues with the battery packs that you can't have a generator too. Wouldn't this generator fall under Article 702?

ARTICLE 702 Optional Standby Systems
I. General
702.1 Scope.
The provisions of this article apply to the installation and operation of optional standby systems.
The systems covered by this article consist of those that are permanently installed in their entirety, including prime movers, and those that are arranged for a connection to a premises wiring system from a portable alternate power supply.
702.2 Definition.
Optional Standby Systems. Those systems intended to supply power to public or private facilities or property where life safety does not depend on the performance of the system. Optional standby systems are intended to supply on-site generated power to selected loads either automatically or manually.
FPN: Optional standby systems are typically installed to provide an alternate source of electric power for such facilities as industrial and commercial buildings, farms, and residences and to serve loads such as heating and refrigeration systems, data processing and communications systems, and industrial processes that, when stopped during any power outage, could cause discomfort, serious interruption of the process, damage to the product or process, or the like.
 
imo you simply have a failure to communicate to them what you are providing. does it clearly state on the plans that this is an optional standby generator, and that the fixtures have internal battery backup (and are thus only to be supplied by normal power sources) ? perhaps you got off on the wrong foot with these folks ?
 
Nakulak, failure to communicate is one of the issues.

Yet, when the person reviewing your plans states the correct way to calculate Title 24 (energy code) for fluorescent fixture is to multiple the lamp wattage by the number of lamps in the fixtures (i.e. 3X32), what knowledge level does that individual have?

Infinity, yes, this generator falls under 702. I tried to get the plans reviewer and the head reviewer to go to 702 and read the section on applicability. I stated the generator can be removed without affect the life safety functions in the building. The response was, we will accept the design if you remove the generator. I tried to explain that we have two normal power sources, but the response was you have utility and a generator and a battery ballast must receive its normal source from utility.

I am experiencing extreme frustration because my plans are being reviewed by persons not completely qualified to review my plans.
 
I?m with you?I agree that you can power a battery ballast with a ?stand-by? generator. No need for separate wiring, independent of normal wiring, etc.

Basically it appears that your reviewer is interpreting ?normal power? as ?utility power??the question is how to persuade them that ?stand-by power? is also ?normal power??Right?

I?m curious to see the inspectors and plan reviewers on the forum?s responses to this and how you would handle an issue like this when there is no reasoning with the AHJ?Do you give-in or can you elevate it to a higher level and if so what is that level?
 
Another thought what if, in a very rare case, utility power is unavailable and now your only power IS ?stand-by power??That should be regarded as normal power now?Right?
 
sadly, I think you will find little help here... the problem is....
During plan review, the reviewer states that in the City of Los Angeles, you cannot connect an optional stand-by generator to the normal power system and it subsequently feed fixtures with unit equipment. There is no requirement stating such that I can find in the Los Angeles Municipal Code (a.k.a. local amendment), California Electrical Code (derivation of the NEC), or the California Building Code (derivation of the IBC).
I am surprised you even got the same answer twice...:rolleyes:
 
Scott
Put in writing what you have installed or propose to install.
Define normal power and utility power.
Reference the NEC for Article 702 in regard to the generator usage.
Reference the Calfornia State Building code and any local amendments for the installation of the unit emergency fixtures.
CC the appropriate people other than the plan review person, everyone has a superior.
If this is not sufficient, you may have to live with the decision.
 
I believe the key thing here in what Pierre' has given is to define what is normal power versus utility power. Many localities will not consider normal power anything other than the "normal" power source to the building during normal operation. Being optional is just that optional and not the normal source.......build your case around that and do as Pierre has stated and in the end he is 100% correct...could just depend on the AHJ's view.
 