I work for a fluorescent lighting manufacturer. My question involves 700.9 (B) exception (2) as it applies to wiring emergency circuits located in fixtures mounted in rows. I want to know if the two scenarios that follow are permissible under exception (2):
1) In a row of fixtures in which every other fixture must be wired to an outside emergency power source (as opposed to an internal emergency battery), is it permissible to provide a single emergency feed separate from the normal feed and passing through those fixtures in the row having only normal power? Must the emergency wiring be separated from the normal wiring by a barrier within the fixture?
2) In a row of fixtures having one lamp per fixture on normal power and one lamp per fixture wired to an outside emergency source, is it permissible to provide one separate feed per row for those lamps on the emergency circuit? Must normal and emergency wiring in the same fixture be separated by a barrier, or can the whole row be treated as in exception (2)?
1) In a row of fixtures in which every other fixture must be wired to an outside emergency power source (as opposed to an internal emergency battery), is it permissible to provide a single emergency feed separate from the normal feed and passing through those fixtures in the row having only normal power? Must the emergency wiring be separated from the normal wiring by a barrier within the fixture?
2) In a row of fixtures having one lamp per fixture on normal power and one lamp per fixture wired to an outside emergency source, is it permissible to provide one separate feed per row for those lamps on the emergency circuit? Must normal and emergency wiring in the same fixture be separated by a barrier, or can the whole row be treated as in exception (2)?