Is it acceptable to run the voltage input for an emon dmon off the same breaker that the emon dmon is monitoring if it is a high amperage breaker?
For instance, lets say I am monitoring a 100 amp breaker with an emon dmon. The terminals for the input voltage of an emon dmon are rated for max #10 wire. The breaker I am monitoring is a 100 amp breaker. Can I run #10's off the 100 amp breaker to the input voltage of the emon dmon if it is less than 10 feet away? Does it fall under the 10' tap rule?
I know the ideal would be to come off a 20 amp breaker of the same panel, but if the panel is maxed out, is this acceptable knowing that the emon dmon will only draw so much amperage?
Thanks
For instance, lets say I am monitoring a 100 amp breaker with an emon dmon. The terminals for the input voltage of an emon dmon are rated for max #10 wire. The breaker I am monitoring is a 100 amp breaker. Can I run #10's off the 100 amp breaker to the input voltage of the emon dmon if it is less than 10 feet away? Does it fall under the 10' tap rule?