EMT across bottom of joists

Status
Not open for further replies.

ChrisFV

Member
Location
NC
Occupation
Electrician Student
Can you run EMT across the bottom of wooden crawl space joists, perpendicular to them? 358.30(B) allows supporting in openings through framing, but is silent about running on bottom of joists.
 
358.30(B) still requires conduit to at least be securely fastened within 3’ feet of termination point.
 
Can you run EMT across the bottom of wooden crawl space joists, perpendicular to them? 358.30(B) allows supporting in openings through framing, but is silent about running on bottom of joists.

The reason for the 358.30(B) rule is two-fold.
1. The end-user of the building might drive fasteners in the framing members after the walls and ceilings are already finished, unaware of the existence of wiring and plumbing within. The nail guard plates are necessary to protect against this error, if your materials are ever closer than the 1.25" limit of expected embedment.
2. The outermost fibers of the structural members carry the greatest load under bending conditions, and are most important to the structural integrity. Aiming your electrical rough-in for holes for the neutral fibers in the center of the member will have the least impact on the structural performance.

Fastening to the underside of floor joists, outside the context of a finished ceiling immediately below, will not introduce either of these issues. Sure it means fasteners thru the outermost structural fibers, but the hole size introduced by a small fastener is nothing compared to the hole you'd have to drill for EMT or other wiring methods.
 