sparkmantoo
Member
- Location
- Virginia
can i run emt and install a piece of lfmc in the run and not have to pull a ground wire? the size of the run is 2" and the lfmc is +/- 18" long. i have to install the lfmc to get from one elevation to another.
A question. Is the flex supported within 12" of each of the terminations?Liquid-tight Flexible Metal Conduit
The following are not considered to be suitable as a grounding means:
1) The 1-1/2 in. and larger trade sizes.
2) The 3/8 and 1/2 in. trade sizes where used on circuits rated higher than 20 amps, or where the total length in the ground return path is greater than 6 ft.
3) The 3/4, 1, and 1-1/4 in. trade sizes where used on circuits rated higher than 60 amps, or where the total length in the ground return path is greater than 6 ft.