dhalleron
Senior Member
- Location
- Louisville, KY
- Occupation
- Master Electrician/Senior Fire Alarm Technician
I have an insurance company questioning me when I said I can't replace a damaged underground EMT feed to a sign with EMT. I said I would need to replace it with something other than EMT such as PVC.
My experience with EMT is it will completely rust out over time when buried. Sometimes it can't handle just being on a wall outside.
Article 358.10 states EMT can be installed in direct contact with the earth where protected by corrosion protection and approved as suitable for the
condition.
This NEMA document states EMT buried in the earth is generally required to have supplementary corrosion protection.
https://www.nema.org/Technical/Documents/UL%20and%20NEC%20Reg%20for%20Corrosion%20Protection%20of%20Steel%20Conduit%20and%20Electrical%20Metalling%20Tubing.pdf
What say you on EMT buried in the earth and what about "supplemental" corrosion protection?
Thanks,