EMT buried in earth

Status
Not open for further replies.

dhalleron

Senior Member
Location
Louisville, KY
Occupation
Master Electrician/Senior Fire Alarm Technician
I have an insurance company questioning me when I said I can't replace a damaged underground EMT feed to a sign with EMT. I said I would need to replace it with something other than EMT such as PVC.

My experience with EMT is it will completely rust out over time when buried. Sometimes it can't handle just being on a wall outside.

Article 358.10 states EMT can be installed in direct contact with the earth where protected by corrosion protection and approved as suitable for the
condition.

This NEMA document states EMT buried in the earth is generally required to have supplementary corrosion protection.
https://www.nema.org/Technical/Documents/UL%20and%20NEC%20Reg%20for%20Corrosion%20Protection%20of%20Steel%20Conduit%20and%20Electrical%20Metalling%20Tubing.pdf

What say you on EMT buried in the earth and what about "supplemental" corrosion protection?

Thanks,
 
IMO, emt will rust out in most environments. I would not install it in the earth especially when we have pvc available
 
Emt is NOT allowed to be buried in earth!! It is a wet location! You need to run rigid pipe. PVC is the obvious choice and a lot cheaper than rigid steel or aluminum.
First I've EVER heard of emt being buried in the ground..
Just tell them the original installation was WRONG!
 
Emt is NOT allowed to be buried in earth!! It is a wet location!

The NEC allows EMT in wet locations.

It also specifically allows EMT underground under certain conditions.


That said, I agree with Dennis, I would not do it, I would use PVC.
 
Emt is NOT allowed to be buried in earth!! It is a wet location! You need to run rigid pipe. PVC is the obvious choice and a lot cheaper than rigid steel or aluminum.
First I've EVER heard of emt being buried in the ground..
Just tell them the original installation was WRONG!

It's allowed, in the US anyway. It is also one of the worst ideas ever.
 
Yeah I know it is stupid. Insurance company wants a better reason than that.

Anyone know what this "supplemental" corrosion protection for buried EMT is?
 
Yeah I know it is stupid. Insurance company wants a better reason than that.

Anyone know what this "supplemental" corrosion protection for buried EMT is?

I think there is a pipe wrap for this application, Fullthrottle (Randy) has mentioned it.

Tell them PVC costs less. :)
 
Tell the INSURANCE company that burried EMT has a tendency to corrode rapidly and chafe the insulation on the wires and SHOCK and ELECTROCUTE people and for a reasonable fee, you can use PVC.
 
Yeah I know it is stupid. Insurance company wants a better reason than that.

Anyone know what this "supplemental" corrosion protection for buried EMT is?

Probably using a sacrificial anode, magnesium alloy most likely. See here. For 1" EMT, likely one per hundred feet is fine, depending on soil conductivity.
 