Is there any restriction on using EMT conduit for 15KV feeder inside the electrical room? This feeder is feeding a primary side transformer for a fire pump.
There are no general restrictions on using EMT for medium voltage conductors, but there are wiring method restrictions for fire pump conductors in Article 695, that may have an impact.